Geaccepteerd antwoordCheck whether the light curtain active level is high level, change it to low level
The controller used for my device is RDV6555G, which has been connected to a grating protection device. However, in actual operation, I tried to block the grating multiple times, but the machine continued to move and did not stop processing. During the inspection process, it was found that the device had no alarm prompts, IO signal feedback was abnormal, and the grating protection function was not effective. How to solve this problem? Thanks.





Kun je deze vraag beantwoorden?
Schrijf je antwoord om anderen met deze vraag te helpen.

Geaccepteerd antwoordCheck whether the light curtain active level is high level, change it to low level






Confirm whether the gate control protection signal line is correctly connected between the control system and the laser. Check if the barrier protection signal circuit is loose, poorly connected, or disconnected.
Check the pin position of the signal line to ensure there are no misconnections.





Heb je een soortgelijke vraag maar geen oplossing gevonden? Plaats je eigen vraag en krijg hulp van de community.

Copyright © 2021 Shenzhen Chanelink Network Technology Co., Ltd. All Rights Reserved.
Yes, I changed it to low level, everything is normal