After my RDC8445S control system started processing, the panel displayed a water protection alarm

seek help! It's frustrating! I turned on the machine today to prepare for cutting the workpiece. I turned on the control system and after starting the processing, the panel displayed a water protection alarm. I tried restarting several times but still couldn't solve the problem. What should I do? RDC8445S

¿Puedes responder esta pregunta?

Escribe tu respuesta para ayudar a quienes tengan la misma duda.

Respuestas (4)

  • Jerome
    Respuesta aceptadaRespuesta aceptada

    Is the water protection level signal set correctly? To set to low level

    1
    Responder
    • You are right. I set the water protection signal to low level, and now there is no alarm

      0
      Responder
  • I think you should check if there is any water seepage or leakage in the equipment and related components of the chiller

    2
    Responder
    • There is no water leakage; the issue lies in the setting of the water protection signal

      0
      Responder
  • Could it be a system false alarm? System firmware or control program abnormalities result in false triggering of waterproof alarms.

     

    1
    Responder
  • Is the wiring of the water protection alarm correct? Someone may make this mistake, please verify

    1
    Responder